No no tell us how you make sure ground loops don't occur in a large multi
floor building with literally hundreds of power consuming devices at a real reasonable cost. "w_tom" wrote in message ... Ground loops is why surge protection must be the single point ground. Problems created by ground loop (the damaged fax machine) is demonstrated by the NIST figure and previously cited discussion in: http://www.epri-peac.com/tutorials/sol01tut.html Which would you believe? Lies promoted by half truths on retail store shelves? Or fact demonstrated by telephone and 911 emergency operators who never need remove headsets during every lightning storm. Effective protection is demonstrated by telephone switching computers that connect to overhead wires everywhere in town. Its not called faith. Its called facts. 1) Demonstrated by theory and 2) proven by example virtually everywhere in the civilized world. Posted was well understood and repeatedly proven even before WWII. One classic myths is that surge protectors operate too slow. Even the GDTs that routinely provided surge protection before WWII and that were much slower were also fast enough for surge protection. These are facts know to those who understood how surge protectors work. 'Surge protector works too slow' is but another myth. Obviously a myth because it is routinely promoted without numbers. One must believe such myths only on faith. notritenoteri wrote: Are you selling lightening protection? You have so much faith. Tell us about ground loops. |
#32
|
|||
|
|||
If I were you I'd be worrying more about the state of the power company's
feed. If you live in a fairly new development say less tha 10 years old its likley to be in pretty good shape. WHere you might have an issue with grounding and the general state of the power grid is on an old neighbourhood. What no one has mentioned is that grounding rods etc eventually corrode. BAck up your data. In my opinion you're worrying about the wrong stuff. I've had a PC at home since the Apple II and never had power surge or brown out problems. I've been wiped out by data loss though because I don't practice what I preach and I was in the Data centre business. "Milleron" wrote in message ... My house was built this year, so its earthing should be up to 1990 national building codes. But how can I be sure the builder did it correctly? I don't think this is anything that the local building inspector can test. I doubt he could tell the difference between a 10-inch grounding rod and one that was driven 20 feet into the ground, if he even inspects this feature at all. How can I tell if my house is earthed correctly? On Fri, 14 Jan 2005 14:28:21 -0500, w_tom wrote: Plug in protectors claim to protect from one type of surge. Do some punching. As one arm swings out, the other withdrawals. That 1-2 punching is an example of a surge that typically does not do damage. Now instead punch with both left and right arms simultaneously. That is the common mode surge that typically damages electronics. Lightning seeks earth ground. It comes down any and all 'arms', passes through punching bag, and exits out other side of punching bag. The plug-in protector does not stop, block, or absorb such destructive surges. IOW it does not sit between surge and the electronics - even though they hope you will assume that. And effective protector connects earlier where wires enter the building so that the 'surge down all wires simultaneously' all find the same earth ground. Lightning in 1752 found earth ground destructively via a church steeple. Franklin simply gave lightning a better path to earth. Lightning is the 'all arms moving forward at the same time" type of surge. You don't stop, block, or filter what miles of sky could not even stop. You 'shunt' lightning to earth ground. That is also what the 'whole house' protector does. It provides lightning with a short path to earth ground. You are surprised how small the Cutler Hammer unit is. It need not be large because it does not stop, block, or absorb the energy. Wire is also not massive because it too carry massive electrical energy and does not try to stop or block it. A surge protector is nothing more than a wire. A wire that conducts only during the rare and short transient. It can be small because the transient is only in microseconds. In a parallel example, try to push a common nail into wood. You cannot. It takes the force of a backhoe to drive that nail. However, we hit that nail with only a 20 oz hammer. Does the human arm have same energy as the backhoe? Of course not. People often confuse energy with power. The hammer has low energy but high power. Lightning has low energy but high power. The protector need not be monstrous because 1) it does not stop or absorb the energy, and 2) the energy is not as massive as urban myths portray. Too many only 'feel' that a lightning strike is high energy. The electrical circuit is best demonstrated by an NIST figure used in an example from: http://www.epri-peac.com/tutorials/sol01tut.html They demonstrate why a fax machine was damaged. Notice that the phone line was not 'earthed' less than 10 feet to the same single point ground as AC electric. Telephone line protector is inside the box labeled NID. The 'whole house' protector is located where 'Arrestor' is labeled. Notice that the destructive surge goes through Arrestor, then to earth ground. Since it need not pass through fax machine to get earth ground, then an AC electric surge does not damage fax machine. All electronic appliances contain effective protection. Anything that is going to work on the end of a power cord (those grossly overpriced plug-in protectors) is already inside electronics - as even required by industry standards. But we worry that internal electronics protection might be overwhelmed. So we install a 'whole house' protector on every incoming utility wire - to same earth ground. Demonstrated in various posts is the AC electric 'whole house' protector (such as the Cutler Hammer), the telco provided protector, and a ground block for cable wire (no protector required). All are only as effective as that earth ground. Now about earthing. Engineered discussed this in two discussions in the newsgroup misc.rural entitled: Storm and Lightning damage in the country 28 Jul 2002 Lightning Nightmares!! 10 Aug 2002 http://tinyurl.com/ghgv and http://tinyurl.com/ghgm Depending on the problem with transients, the earth ground may need be enhanced. Important is the neighborhood history. Also important is the geology. Does the ground tend to attract more CG lightning? For example, mid-west storms may be spectacular, but most of the lightning remains sky to sky. WV is a region with high numbers of CG (cloud to ground) strikes per thunderstorm. Those discussions also mention equipotential which is why Ufer grounds and halo grounds make the protector even more effective. Also is earth conductive or is it sand. I believe that previous discussion also tells a story of a house struck multiple times - and lightning rods did not work. Why? Lightning rods were earthed poorly in non-conductive sand. Bottom line - a surge protector is only as effective as its earth ground. In most locations, a single ground rod may provide massive increase in protection. A house that does not at least meet post 1990 National Electrical Code earthing requirements does not have the necessary earth ground. Also in that misc.rural discussion would be how wire must be routed. For example, no sharp bends and no splices. A ground wire bundled with other wires may only induce more surges on that other wire (which is but another reason why plug-in protectors have no effective earth ground). There is much to read. Come back with questions. The simple earthing of surges is surprisingly not intuitively obvious. In discussing this, I was amazed how many don't even know what a Ben Franklin air terminal (lightning rod) does - AND yet would recommend surge protectors. Many even argue pointed verse blunt lighting rods - when earth ground defines the effectiveness of that rod. A surge protector is only as effective as its earth ground. snip Ron |
#33
|
|||
|
|||
Lets assume a protector adjacent to a computer will earth a
100 amp transient via that wall receptacle. Due to wire impedance, that 50 foot of 12 AWG wire (back to circuit breaker box) may be about 130 ohms impedance (not resistance - impedance). 100 amps times 130 ohms is 13,000 volts. Will that 100 amp transient find earth ground via 13,000 volts of wire? Of course not. Those 100 amps will find other (destructive) paths to earth ground such as through a mouse wire touching the baseboard heat and via the computer's modem. Notice how a modem is damaged. Furthermore, if that 50 foot of 12 AWG wire is earthing a 100 amp transient, then that ground wire induces transients on all adjacent wires. Now we have surges on other equipment thanks to that plug-in protector. Where is the protection? How does that 130 ohm impedance of wire create an earth ground AND not create induced transients? Wall receptacle does not provide an earth ground. Just another reason why the plug-in protector manufacturer fears to even discuss earthing. That wall receptacle (and plug-in protector) has all but no earth ground. And as we know even from pre-WWII GE and Westinghouse science papers - no earth ground means no effective protection. Wall receptacles provide 'safety' or 'equipment' ground. They are not 'earth ground' due to too much wire impedance. Wire impedance is a basic electrical concept that plug-in protector manufacturers hope you will not learn - to sell their ineffective, undersized, and overpriced product to the naive. Why must a 'whole house' protector make a 'less than 10 foot' connection to earth ground? Why must earthing wire have no sharp bends and no splices and not be inside metallic conduit? Why must the earthing wire remain separated from other wires? Same reasons that a wall receptacle is not earth ground. No earth ground means no effective protection. So plug-in manufacturers avoid the entire topic hoping others will promote myths. Leythos has promoted that myth: "Every outlet in the house has a earth ground ..." What does a ground fault indicator on that UPS report? It reports a defective safety ground. It cannot report a good safety ground. It can only report when the safety ground is defective. Furthermore, that UPS ground indicator says nothing - zero - about earth ground. But they hope others will confuse the word 'ground' with 'earth' to promote protector myths. Leythos wrote: My house, built in the early 70's, here in the USA, has a large ground rod just outside the house, within about 4' of the breaker panel. Every outlet in the house has a earth ground in addition to the neutral (three prong receptacles). Each of my UPS's has ground fault indicator. I'll keep using the APC UPS's I have, I've seen what happens when people don't protect their electronics. |
#34
|
|||
|
|||
To understand a surge, one must first draw a complete
electric circuit. Charges from a cloud may fall 4 kilometers to the east. Now a cloud must connect those cloud borne charges to earth borne charges. What, electrically, is the shortest path? 5 kilometers diagonally? Of course not. The shortest electrical path is 3 kilometers directly down to AC electric utility wires. Then 2 kilometers east through underground (or overhead) utility wires to the end of the block. Then through transformer (or household appliances) into earth. Then another 2 kilometers east through earth to those earth borne charges. Now we have a complete circuit. Anything that has both an incoming and outgoing path in that circuit may be damaged. Homes are the end of a utility distribution system may become an incoming and outgoing path in that circuit. Other transformers may have been an incoming path. But with no outgoing electrical path, those other transformers would suffer no damage. Some then assume lightning is capricious. Reality: those humans failed to first remember their elementary school science. Both incoming and outgoing path must exist to have electricity flow. Electricity of a destructive surge would only pass through the last transformer. Milleron wrote: Interesting point about being the last house on the street. Several years ago, we had a nasty summer electrical storm in central Ohio that knocked out power to many homes and neighborhoods. We had no lightning real close to my house, but we lost power. We have underground wiring with transformers every so often. I'm sure it's exactly like overhead wires. At any rate the crew that came out pointed out that our transformer was the LAST one in a long chain. They thought the strike was distant and surged all the way to that point. It ruined our transformer (took 30 hours to replace it), but there was no damage at all in any of the houses that drew power from that particular transformer. What happened in this scenario? If the surge went to earth at that point, what killed the transformer without hurting any of the transformers farther up the line? |
#35
|
|||
|
|||
How did the 100 amps get to the wall receptacle? Assuming that it came
from outside, then, by exactly the same 'logic' that you are using, it should have been grounded through "other paths to earth ground" long before it got there. If lightning is going to strike your computer room, or even (probably) your house, under which circumstances your example might be more realistic, there is probably little you can do to save your hardware. If you calculate _instantaneous_ charge flow at a wall socket at the peak of a big, lightning-induced, transient, you may come up with tens or hundreds of amps as an answer, but it isn't really helpful or meaningful to use normal concepts of current flow in thinking about very short (microseconds) transients. In any event, no protective device will block 100% of a transient (true UPSes possible excepted, since they should totally disconnect the mains from the supplied device). The object of in-line surge suppressors is to provide a sufficiently low impedance path to ground for the peak of the transient that the power that gets through via the (typically much higher impedance) path through the protected equipment is not sufficient to do damage. It's like home security - the object there is not to make your house thief-proof, which is next to impossible, but to make it sufficiently challenging for the potential thief that (s)he will look elsewhere. On Sun, 16 Jan 2005 03:34:55 -0500, w_tom wrote: Lets assume a protector adjacent to a computer will earth a 100 amp transient via that wall receptacle. Due to wire impedance, that 50 foot of 12 AWG wire (back to circuit breaker box) may be about 130 ohms impedance (not resistance - impedance). 100 amps times 130 ohms is 13,000 volts. Will that 100 amp transient find earth ground via 13,000 volts of wire? Of course not. Those 100 amps will find other (destructive) paths to earth ground such as through a mouse wire touching the baseboard heat and via the computer's modem. Notice how a modem is damaged. Furthermore, if that 50 foot of 12 AWG wire is earthing a 100 amp transient, then that ground wire induces transients on all adjacent wires. Now we have surges on other equipment thanks to that plug-in protector. Where is the protection? How does that 130 ohm impedance of wire create an earth ground AND not create induced transients? Wall receptacle does not provide an earth ground. Just another reason why the plug-in protector manufacturer fears to even discuss earthing. That wall receptacle (and plug-in protector) has all but no earth ground. And as we know even from pre-WWII GE and Westinghouse science papers - no earth ground means no effective protection. Wall receptacles provide 'safety' or 'equipment' ground. They are not 'earth ground' due to too much wire impedance. Wire impedance is a basic electrical concept that plug-in protector manufacturers hope you will not learn - to sell their ineffective, undersized, and overpriced product to the naive. Why must a 'whole house' protector make a 'less than 10 foot' connection to earth ground? Why must earthing wire have no sharp bends and no splices and not be inside metallic conduit? Why must the earthing wire remain separated from other wires? Same reasons that a wall receptacle is not earth ground. No earth ground means no effective protection. So plug-in manufacturers avoid the entire topic hoping others will promote myths. Leythos has promoted that myth: "Every outlet in the house has a earth ground ..." What does a ground fault indicator on that UPS report? It reports a defective safety ground. It cannot report a good safety ground. It can only report when the safety ground is defective. Furthermore, that UPS ground indicator says nothing - zero - about earth ground. But they hope others will confuse the word 'ground' with 'earth' to promote protector myths. Leythos wrote: My house, built in the early 70's, here in the USA, has a large ground rod just outside the house, within about 4' of the breaker panel. Every outlet in the house has a earth ground in addition to the neutral (three prong receptacles). Each of my UPS's has ground fault indicator. I'll keep using the APC UPS's I have, I've seen what happens when people don't protect their electronics. Please respond to the Newsgroup, so that others may benefit from the exchange. Peter R. Fletcher |
#36
|
|||
|
|||
This whole discussion is turning into a big show-boat of technical
knowledge. Somebody went to college I went to college too two degrees worth and I managed a university data centre for 17 years I've spent most of my career in the IT industry mostly in telecom and facilities management. I don't know bugger all, really. Anecdotal evidence, racial memories or whatever you want to call it suggest lightening and surges aren't a problem at least in my part of the world. What I do know is that in North America in Canada where I live which believe it or not has lightening storms even in January, lightening is a minor inconvenience with the standards that are in place. Interruption of service is an issue but a real UPS with the proper maintenance (both money issues not problems) will solve that. The big deal is loss of data. Whoever started this thread is worrying about the wrong thing in my opinion but hey that's what salesmen count on. "w_tom" wrote in message ... Lets assume a protector adjacent to a computer will earth a 100 amp transient via that wall receptacle. Due to wire impedance, that 50 foot of 12 AWG wire (back to circuit breaker box) may be about 130 ohms impedance (not resistance - impedance). 100 amps times 130 ohms is 13,000 volts. Will that 100 amp transient find earth ground via 13,000 volts of wire? Of course not. Those 100 amps will find other (destructive) paths to earth ground such as through a mouse wire touching the baseboard heat and via the computer's modem. Notice how a modem is damaged. Furthermore, if that 50 foot of 12 AWG wire is earthing a 100 amp transient, then that ground wire induces transients on all adjacent wires. Now we have surges on other equipment thanks to that plug-in protector. Where is the protection? How does that 130 ohm impedance of wire create an earth ground AND not create induced transients? Wall receptacle does not provide an earth ground. Just another reason why the plug-in protector manufacturer fears to even discuss earthing. That wall receptacle (and plug-in protector) has all but no earth ground. And as we know even from pre-WWII GE and Westinghouse science papers - no earth ground means no effective protection. Wall receptacles provide 'safety' or 'equipment' ground. They are not 'earth ground' due to too much wire impedance. Wire impedance is a basic electrical concept that plug-in protector manufacturers hope you will not learn - to sell their ineffective, undersized, and overpriced product to the naive. Why must a 'whole house' protector make a 'less than 10 foot' connection to earth ground? Why must earthing wire have no sharp bends and no splices and not be inside metallic conduit? Why must the earthing wire remain separated from other wires? Same reasons that a wall receptacle is not earth ground. No earth ground means no effective protection. So plug-in manufacturers avoid the entire topic hoping others will promote myths. Leythos has promoted that myth: "Every outlet in the house has a earth ground ..." What does a ground fault indicator on that UPS report? It reports a defective safety ground. It cannot report a good safety ground. It can only report when the safety ground is defective. Furthermore, that UPS ground indicator says nothing - zero - about earth ground. But they hope others will confuse the word 'ground' with 'earth' to promote protector myths. Leythos wrote: My house, built in the early 70's, here in the USA, has a large ground rod just outside the house, within about 4' of the breaker panel. Every outlet in the house has a earth ground in addition to the neutral (three prong receptacles). Each of my UPS's has ground fault indicator. I'll keep using the APC UPS's I have, I've seen what happens when people don't protect their electronics. |
#37
|
|||
|
|||
How does 100 amps get to a wall receptacle? Destructive
transients are current sources. That means voltage will increase, as necessary, to maintain that 100 amps. If 100 amps into the protector and adjacent computer requires thousands of volts, then thousands of volts will be provided. However if something else closer makes the earth ground connection, then voltage need not increase to maintain 100 amps. Instead that closer computer, or TV, or modem becomes the destroyed appliance. If permitted inside a building, that surge will find some destructive path to earth ground via appliances. This is called a direct strike. Human failure is required to permit a surge inside the building. If lightning strikes your house - IOW strikes AC electric wires on a utility pole - AND if electronic damage occurs, then you (the human) are reason for that failure. Two reasons. 1) Because effective surge protection is available, so effective, and understood for so long. 2) Because effective surge protection is so inexpensive - tens of times less money per appliance compared to plug-in protectors. Don't post this myth: "no protective device will block 100% of a transient". Only mythical protectors block, stop, filter or absorb destructive transients. Effective protectors 'shunt' surges. That means an effective protector is located at the service entrance AND connected 'less than 10 foot' to earth ground. So effective and so inexpensive that surge damage is considered unnecessary. You need not install such protection. No law requires it. But it is grossly irresponsible to tell others that no protector device will work. They worked just fine even before WWII, as even demonstrated in peer reviewed science papers. The Empire State Building is struck about 25 times per year. Where is all the FM and TV electronics damage? Why does a 'building wide' (real) UPS provide protection? UPS also does not stop, block or absorb surges. Again, those verbs would only promote myths. The 'real' UPS includes a 'whole house' protector circuit. A UPS that does provide effective protection is also typically connected 'less than 10 foot' to single point earth ground. Same principles apply. A protector adjacent to appliances does not provide effective protection, is typically undersized, and costs tens of times more money per protected appliance. How to identify the ineffective protector? 1) It has no dedicated earthing connection AND 2) it avoids all discussion about earthing. Two simple statements identify effective protection. How to install effective protection? Spend less money. Use well proven human knowledge. Earth before destructive transients can enter a building. Never think a surge protector will stop or block surges no matter how often that myth is promoted. A surge protector is only as effective as its earth ground. "Peter R. Fletcher" wrote: How did the 100 amps get to the wall receptacle? Assuming that it came from outside, then, by exactly the same 'logic' that you are using, it should have been grounded through "other paths to earth ground" long before it got there. If lightning is going to strike your computer room, or even (probably) your house, under which circumstances your example might be more realistic, there is probably little you can do to save your hardware. If you calculate _instantaneous_ charge flow at a wall socket at the peak of a big, lightning-induced, transient, you may come up with tens or hundreds of amps as an answer, but it isn't really helpful or meaningful to use normal concepts of current flow in thinking about very short (microseconds) transients. In any event, no protective device will block 100% of a transient (true UPSes possible excepted, since they should totally disconnect the mains from the supplied device). The object of in-line surge suppressors is to provide a sufficiently low impedance path to ground for the peak of the transient that the power that gets through via the (typically much higher impedance) path through the protected equipment is not sufficient to do damage. It's like home security - the object there is not to make your house thief-proof, which is next to impossible, but to make it sufficiently challenging for the potential thief that (s)he will look elsewhere. |
#38
|
|||
|
|||
If power loss creates damage, then what electronic parts are
damaged? To claim a blackout causes damage means failed electronic parts are identified. I do this. I learned by replacing parts AND tracing the destructive circuit to its source. Power loss damages computer hardware when a human buys defective hardware - often because he 'saved' money. An electrician temporarily disconnecting a neutral wire can also destroy electronics. Was that damage from the resulting blackout? No. Blackout was only another symptom of the failure. Too many only assume damage was created by the blackout only because damaged happened. This is how junk science reasoning gets promoted. Purpose of an adjacent UPS is as notritenoteri has posted: to protect data. A plug-in UPS contains same protector circuit found in power strip protectors. How do you know? The numbers. Review numbers on both that plug-in UPS and for power strip protector. What are both protector circuits rated in? Joules. Why? They both use the same protector circuit. Why is a plug-in UPS any better than a power strip protector? It is not. They both have the same protector circuit. IOW they both claim the same ineffective protection. Neither provides superior protection. You want 'data' protection? Install the UPS. You want 'hardware' protection? Earth ground every incoming utility wire either by direct hardwire connection or via a surge protector. Some earthing connections are even required by electrical codes. Power loss does not damage hardware. Unfortunately much computer hardware purchased by computer assemblers is defective by design - as demonstrated by what is damaged. The original poster asked how to prolong an Asus motherboard. One solution starts with power supply selection. Many power supplies installed by computer assemblers are missing essential functions. Inferior supplies may even fail during power loss. Many essential power supply functions may exist only if the manufacturer includes a long list of numeric specs. Numbered specs are essential. But again, these numbers are too complex for those computer assemblers who instead may blame a blackout. No numeric specifications with that power supply? Then expect weird failures - such as damage created by a blackout or even Asus motherboard damage. Leythos wrote: I agree with the above, and I was pretty sure that I said the same thing - power loss is what we experience the most, and uncontrolled power loss does impact the life expectancy of the hardware systems. |
#39
|
|||
|
|||
What is comes down to is simply this ... and this is always
a source of disagreement. Engineers first learn both the underlying theory of what happens AND also identify the failure at each individual component. It is the standard requirement of understanding the problem both theoretically and experimentally. That is called science. Sometimes a technician will see a failure, see that it coincided with an event, and the associate the two as same. And so we have this myth about power blackouts causing hardware problems. Blackout and voltage sags (brownouts) do not harm hardware. UPSes may be helpful for hardware protection WHEN that hardware is defective. One source of motherboard damage are power supplies that do not contain essential functions. Power supplies often purchased by computer assemblers who only understand one number - price. If a blackout or brownout causes hardware damage or other power related service calls, then the hardware was defective when purchased and installed by that shameful computer assembler. Some details. Just because a UPS has a joules rating does not mean it features protection. Basic technical knowledge would make that obvious. UPSes and power strip protectors both have joules ratings. IOW both provide same protection using same protector circuit. Both provide same ineffective protection for the same repeated reason using the same circuit. Power supplies have no warning about power cycling because power cycling is not a problem to properly designed power supplies. In the world of rumors, power cycling causes damage. Again, that can occur when hardware is missing essential functions that were common even 30 years ago. It is a problem created by bean counter mentalities who promote themselves as computer experts. You can blame problems on anything but the human. Its easy. The user would not know differently. And unfortunately, either do so many computer assemblers who never even learned basic functions of power supplies and UPSes. For example, the Ground Fault Indicator does not say anything about earth ground. Its function is not relevant to anything in this discussion. To test earth ground, the UPS would require a complete electric circuit through Earth ground. Where is the complete circuit through Earth ground? It does not exist - obviously it does not exist. That Ground Fault indicator only reports a defective SAFETY ground. Safety ground is different from earth ground even though both share some components. Furthermore, that Ground Fault Indicator cannot even report a good Safety ground. It can only report when the Safety ground is defective AND says absolutely nothing about Earth ground. But the Ground Fault Indicator can have technicians confusing Safety ground with Earth ground to promote the myths about hardware protection. A plug-in UPS is only for data protection. Hardware protection of the Asus motherboard is provided by things such as a 'whole house' protector AND by a power supply that actually meets Intel specs - requirements that were standard even 30 years ago. Many power supplies today do not even contain functions considered essential 30 years ago. That would explain hardware damage and other power related problems. Leythos wrote: You know, what it really comes down to is this: Like it or not, those crude devices you say have no merit, actually save people from data loss and hardware loss more times that I can count. Not every cheap PSU comes with a warning about cycling AC power source to many times or too frequently, in fact, I don't know of ANY PSU that comes with that warning. It's still a simple matter of experience in most cases a UPS (residential device connected to a line with ground) is going to be of more benefit that not having the device. When I was at the local computer store today I looked at every unit, all but one claimed joules protection level, most had ground fault indicators and reverse polarity indicators (meaning a swapped hot/neut). As a good example of how well a UPS works, we had a new client that had no UPS's in their buildings - not one and 70+ computers. On the average they required service related to power problems at least once a week (8 buildings across the USA). After installing the UPS's at each device, there were no more power related service calls, not more lost data, and no more devices that were "broken" by storms. Even when other hardware in the buildings, not protected by a UPS was damaged, the computers protected by them were fine. So, you can list all the technical spec's, the NEC, and anything else you want, but the simple fact is that a UPS, even a cheap one, will pay for itself after the first power outage or other event where the systems survive. |
#40
|
|||
|
|||
"Blackout and voltage sags (brownouts) do not harm hardware." where is this
axiom written? Science you say? More like junk science. This NG is full of people with problems that was caused by everything from bad design to the wind. How much practical experience have you had I'm curious. I obviously live on another planet where the techies are mostly concerned about fixing the problem. You tell me where I can get one of these power supplies that is guaranteed not to be responsible in any fashion whatsover for problems caused by blackouts or brown outs. I haven't heard of any but I don't know many of the answers in fact I don't know most of them. WHat an advertising advantage "we guarantee our power supplies are perfect in the event of blackouts or brownouts" . "w_tom" wrote in message ... What is comes down to is simply this ... and this is always a source of disagreement. Engineers first learn both the underlying theory of what happens AND also identify the failure at each individual component. It is the standard requirement of understanding the problem both theoretically and experimentally. That is called science. Sometimes a technician will see a failure, see that it coincided with an event, and the associate the two as same. And so we have this myth about power blackouts causing hardware problems. Blackout and voltage sags (brownouts) do not harm hardware. UPSes may be helpful for hardware protection WHEN that hardware is defective. One source of motherboard damage are power supplies that do not contain essential functions. Power supplies often purchased by computer assemblers who only understand one number - price. If a blackout or brownout causes hardware damage or other power related service calls, then the hardware was defective when purchased and installed by that shameful computer assembler. Some details. Just because a UPS has a joules rating does not mean it features protection. Basic technical knowledge would make that obvious. UPSes and power strip protectors both have joules ratings. IOW both provide same protection using same protector circuit. Both provide same ineffective protection for the same repeated reason using the same circuit. Power supplies have no warning about power cycling because power cycling is not a problem to properly designed power supplies. In the world of rumors, power cycling causes damage. Again, that can occur when hardware is missing essential functions that were common even 30 years ago. It is a problem created by bean counter mentalities who promote themselves as computer experts. You can blame problems on anything but the human. Its easy. The user would not know differently. And unfortunately, either do so many computer assemblers who never even learned basic functions of power supplies and UPSes. For example, the Ground Fault Indicator does not say anything about earth ground. Its function is not relevant to anything in this discussion. To test earth ground, the UPS would require a complete electric circuit through Earth ground. Where is the complete circuit through Earth ground? It does not exist - obviously it does not exist. That Ground Fault indicator only reports a defective SAFETY ground. Safety ground is different from earth ground even though both share some components. Furthermore, that Ground Fault Indicator cannot even report a good Safety ground. It can only report when the Safety ground is defective AND says absolutely nothing about Earth ground. But the Ground Fault Indicator can have technicians confusing Safety ground with Earth ground to promote the myths about hardware protection. A plug-in UPS is only for data protection. Hardware protection of the Asus motherboard is provided by things such as a 'whole house' protector AND by a power supply that actually meets Intel specs - requirements that were standard even 30 years ago. Many power supplies today do not even contain functions considered essential 30 years ago. That would explain hardware damage and other power related problems. Leythos wrote: You know, what it really comes down to is this: Like it or not, those crude devices you say have no merit, actually save people from data loss and hardware loss more times that I can count. Not every cheap PSU comes with a warning about cycling AC power source to many times or too frequently, in fact, I don't know of ANY PSU that comes with that warning. It's still a simple matter of experience in most cases a UPS (residential device connected to a line with ground) is going to be of more benefit that not having the device. When I was at the local computer store today I looked at every unit, all but one claimed joules protection level, most had ground fault indicators and reverse polarity indicators (meaning a swapped hot/neut). As a good example of how well a UPS works, we had a new client that had no UPS's in their buildings - not one and 70+ computers. On the average they required service related to power problems at least once a week (8 buildings across the USA). After installing the UPS's at each device, there were no more power related service calls, not more lost data, and no more devices that were "broken" by storms. Even when other hardware in the buildings, not protected by a UPS was damaged, the computers protected by them were fine. So, you can list all the technical spec's, the NEC, and anything else you want, but the simple fact is that a UPS, even a cheap one, will pay for itself after the first power outage or other event where the systems survive. |
Thread Tools | |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Thread Starter | Forum | Replies | Last Post |
Cleaning CD & DVD drives [Was: What's the life expectancy of a DVD drive?] | Phred | Cdr | 3 | June 23rd 04 07:48 AM |
USB Keyboards: Recommendations for & Life Expectancy of | limner | Homebuilt PC's | 0 | April 7th 04 01:59 AM |
Life expectancy of a burner? | farqua | Cdr | 6 | January 29th 04 04:03 PM |
Life expectancy of IDE disk | Moonlit | Homebuilt PC's | 8 | July 6th 03 07:00 PM |