Open rack vs. enclosed cabinet
I'm looking to move my servers to a rack/cabinet in a 7-ft by 5.5-ft room.
About 6 tower servers, 1 rack server, 4 rack switches, 3 routers/telecom, and 3 non-rack UPS. Would an enclosed cabinet work in terms of cooling? Any general recommendations of open rack vs. enclosed cabinet? Not much literature on the topic... -- Yoann Roman |
#2
|
|||
|
|||
thats like physical security, but i'm not expert when it comes to that
Yoann Roman wrote: I'm looking to move my servers to a rack/cabinet in a 7-ft by 5.5-ft room. About 6 tower servers, 1 rack server, 4 rack switches, 3 routers/telecom, and 3 non-rack UPS. Would an enclosed cabinet work in terms of cooling? Any general recommendations of open rack vs. enclosed cabinet? Not much literature on the topic... -- Yoann Roman |
#3
|
|||
|
|||
My own experience has been that wire mesh shelving is best - affords
greatest flexibility, easy wire routing, few ventilation problems. This is the sort of thing I'd recommend: http://safcoshelving.com/shop/prodty...ageHistory=cat Available anywhere - google on wire shelving Racks are good for rack servers, rack routers, etc. but not great for towers. Yoann Roman wrote: I'm looking to move my servers to a rack/cabinet in a 7-ft by 5.5-ft room. About 6 tower servers, 1 rack server, 4 rack switches, 3 routers/telecom, and 3 non-rack UPS. Would an enclosed cabinet work in terms of cooling? Any general recommendations of open rack vs. enclosed cabinet? Not much literature on the topic... |
#4
|
|||
|
|||
My own experience has been that wire mesh shelving is best - affords
greatest flexibility, easy wire routing, few ventilation problems. This is the sort of thing I'd recommend: http://safcoshelving.com/shop/prodty...ageHistory=cat Available anywhere - google on wire shelving Racks are good for rack servers, rack routers, etc. but not great for towers. My problem is that the room is fairly small (7 ft. by 5.5 ft) so I would prefer to have only one solution. I could stack all the rack-based equipment, but that wouldn't be a very neat solution, IMO. -- Yoann Roman |
#5
|
|||
|
|||
thats like physical security, but i'm not expert when it comes to that
Physical security seems to be the main argument for enclosed cabinets, whereas better ventilation and easier access to components seems to be the argument for open racks. But I see those two argued for enclosed cabinets, too. And it seems that secured environments I've seen still use enclosed cabinets, so I figured there must be another reason to have them. -- Yoann Roman |
#6
|
|||
|
|||
On Wed, 7 Sep 2005 17:58:46 -0400, "Yoann Roman"
wrote: I'm looking to move my servers to a rack/cabinet in a 7-ft by 5.5-ft room. About 6 tower servers, 1 rack server, 4 rack switches, 3 routers/telecom, and 3 non-rack UPS. Would an enclosed cabinet work in terms of cooling? Any general recommendations of open rack vs. enclosed cabinet? Not much literature on the topic... A closed cabinet needs sufficient forced air (fan(s)) to deal with the thermal load and placement of components in it. It is not just a matter of open or closed cabinet but the exact equipment, placement, and closed rack. In general, either option can work, but- The room itself also needs active airflow. It is not enough to just have an HVAC duct that only moves air when temp deviates. If you had a failsafe 100% on-time blower for the HVAC and large enough ductwork, it could suffice but generally one looks at supplimental cooling local to the room... and the way that's implemented can have a lot to do with the area surrounding the room, the ceiling above or floor below, and acceptible noise levels and/or noise isolation. Either way you approach the racks or cabinets, the room tends to need similar ventilation rate, or to put it another way, sufficient rate and a little excess is better than too little. The system/component chassis themselves are generally not meant to aid in cooling, so whether that chassis is exposed to outside air or not matters little relative to the front intake and rear exhaust potential of whatever you choose. For example, either way the cooling will be worse if you put several butted-up against a corner wall(s). Some air will recirculate and how much of an impact that has can depend on the ambient room temp. Air-conditioning is desirable. |
#7
|
|||
|
|||
and keep in mind that HVAC may be turned off at nights, weekends,
holidays. If the equipment is 24/7, the environment must also be suitable 24/7. To judge whether you need extra A/C or ventilation, put an electric space heater (or two) into the room and see how hot it gets - they typically output ~1300-1500 watts as heat. The PCs are each putting out ~100-300 watts of heat; the networking gear adds some more; ditto any VDTs. As for physical security, a metal or solid core door with a key which you control affords much more security than a rack with a cheap cabinet lock that is better suited to protecting a desk drawer from pencil theft. kony wrote: On Wed, 7 Sep 2005 17:58:46 -0400, "Yoann Roman" wrote: I'm looking to move my servers to a rack/cabinet in a 7-ft by 5.5-ft room. About 6 tower servers, 1 rack server, 4 rack switches, 3 routers/telecom, and 3 non-rack UPS. Would an enclosed cabinet work in terms of cooling? Any general recommendations of open rack vs. enclosed cabinet? Not much literature on the topic... A closed cabinet needs sufficient forced air (fan(s)) to deal with the thermal load and placement of components in it. It is not just a matter of open or closed cabinet but the exact equipment, placement, and closed rack. In general, either option can work, but- The room itself also needs active airflow. It is not enough to just have an HVAC duct that only moves air when temp deviates. If you had a failsafe 100% on-time blower for the HVAC and large enough ductwork, it could suffice but generally one looks at supplimental cooling local to the room... and the way that's implemented can have a lot to do with the area surrounding the room, the ceiling above or floor below, and acceptible noise levels and/or noise isolation. Either way you approach the racks or cabinets, the room tends to need similar ventilation rate, or to put it another way, sufficient rate and a little excess is better than too little. The system/component chassis themselves are generally not meant to aid in cooling, so whether that chassis is exposed to outside air or not matters little relative to the front intake and rear exhaust potential of whatever you choose. For example, either way the cooling will be worse if you put several butted-up against a corner wall(s). Some air will recirculate and how much of an impact that has can depend on the ambient room temp. Air-conditioning is desirable. |
#8
|
|||
|
|||
and keep in mind that HVAC may be turned off at nights, weekends,
holidays. If the equipment is 24/7, the environment must also be suitable 24/7. To judge whether you need extra A/C or ventilation, put an electric space heater (or two) into the room and see how hot it gets - they typically output ~1300-1500 watts as heat. The PCs are each putting out ~100-300 watts of heat; the networking gear adds some more; ditto any VDTs. As for physical security, a metal or solid core door with a key which you control affords much more security than a rack with a cheap cabinet lock that is better suited to protecting a desk drawer from pencil theft. Thank you both for your input. Physical security is not a concern here. The room locks and access to the key is controlled. The environment is secure enough for the application, too. My main concerns a - to protect the equipment from general dust - provide a stable physical environment (safe from bumps, hits, etc...) - have a setup that allows easy maintenance and setup, but nothing regular - protect against accidental pulling of cables (the room is also the telco closet open to telco companies) This is a small/medium business, as you can tell by the number of servers, so cost is the key. Dedicated HVAC is probably hard to obtain from the building. Regular HVAC is never shut off during the year, though. There will be a duct added to the room. If air flow became a problem, maybe some of APC's air flow products would help, although the room has no raised floor. It has tiled ceilings, but I don't think there is much air circulation up there. This will be the only rack/cabinet in the room and I figured I could center it so that it had plenty of space on all sides. The rack I'm looking at is a SMC rack on casters with fully perforated rear door, fan at the top, and perforated sides on either side of the front door's plexiglass. With a 42U rack/cabinet, I think I could guarantee at least 1U of space between each component. I didn't notice any component giving off much heat other than the UPS's. I realize this is no where near the ideal data center, but I don't think the hardware/application demands that type of setup, right? -- Yoann Roman |
#9
|
|||
|
|||
On Thu, 8 Sep 2005 11:35:41 -0400, "Yoann Roman"
wrote: My main concerns a - to protect the equipment from general dust Air filtration can be necessary. Could be whole-room, could be on a sealed cabinet, either way if this is a dusty environment then a service interval needs to be maintained for the filter inspection and/or replacement. - provide a stable physical environment (safe from bumps, hits, etc...) If people are getting in and hitting the racks, you need better locks or a guard or pre-employment screening or something of this nature. - have a setup that allows easy maintenance and setup, but nothing regular - protect against accidental pulling of cables (the room is also the telco closet open to telco companies) You can partition things off, demand a telco check-in and supervision, or have insurance cover any damage, yours or theirs. It's not a large room so is there even space for everything you need in it and still the realistic expectation that a stranger can walk in and service something? Depends on where you situate everything. We can't easily do that or advise on it. This is a small/medium business, as you can tell by the number of servers, so cost is the key. Dedicated HVAC is probably hard to obtain from the building. Regular HVAC is never shut off during the year, though. There will be a duct added to the room. I suggest not only a duct but fan local to the room. If air flow became a problem, maybe some of APC's air flow products would help, although the room has no raised floor. It has tiled ceilings, but I don't think there is much air circulation up there. There's where a fan comes in. If the fan is exhausting into the ceiling, then there is air circulation... providing the room isn't so sealed off that no air gets in but HVAC duct will help there too. In other words with a localized AC system the room can be fairly well sealed (except the back-end of the AC unit itself) but without localized AC, you'll want the room not so well sealed up, meaning typical doors over carpeted areas are too much restriction without *something* else to allow that flow while still keeping the room secure. This will be the only rack/cabinet in the room and I figured I could center it so that it had plenty of space on all sides. The rack I'm looking at is a SMC rack on casters with fully perforated rear door, fan at the top, and perforated sides on either side of the front door's plexiglass. With a 42U rack/cabinet, I think I could guarantee at least 1U of space between each component. I didn't notice any component giving off much heat other than the UPS's. Are any of these passively cooled devices? If not, space between racks should not be an issue, each component should be self-sufficient in cooing providing the ambient (intake) air temp is low enough. I realize this is no where near the ideal data center, but I don't think the hardware/application demands that type of setup, right? Same environment, smaller scale. |
#10
|
|||
|
|||
Are any of the adjoining spaces unoccupied? Perhaps, you could put a
window A/C through a wall and dump the heat 'next door'. kony wrote: On Thu, 8 Sep 2005 11:35:41 -0400, "Yoann Roman" wrote: My main concerns a - to protect the equipment from general dust Air filtration can be necessary. Could be whole-room, could be on a sealed cabinet, either way if this is a dusty environment then a service interval needs to be maintained for the filter inspection and/or replacement. - provide a stable physical environment (safe from bumps, hits, etc...) If people are getting in and hitting the racks, you need better locks or a guard or pre-employment screening or something of this nature. - have a setup that allows easy maintenance and setup, but nothing regular - protect against accidental pulling of cables (the room is also the telco closet open to telco companies) You can partition things off, demand a telco check-in and supervision, or have insurance cover any damage, yours or theirs. It's not a large room so is there even space for everything you need in it and still the realistic expectation that a stranger can walk in and service something? Depends on where you situate everything. We can't easily do that or advise on it. This is a small/medium business, as you can tell by the number of servers, so cost is the key. Dedicated HVAC is probably hard to obtain from the building. Regular HVAC is never shut off during the year, though. There will be a duct added to the room. Unclear what you mean here - You need both a supply duct (will it supply cold air during the winter heating season?) and a return air duct - something that will draw the air you've heated up out of the room. I suggest not only a duct but fan local to the room. If air flow became a problem, maybe some of APC's air flow products would help, although the room has no raised floor. It has tiled ceilings, but I don't think there is much air circulation up there. There's where a fan comes in. If the fan is exhausting into the ceiling, then there is air circulation... providing the room isn't so sealed off that no air gets in but HVAC duct will help there too. In other words with a localized AC system the room can be fairly well sealed (except the back-end of the AC unit itself) but without localized AC, you'll want the room not so well sealed up, meaning typical doors over carpeted areas are too much restriction without *something* else to allow that flow while still keeping the room secure. This will be the only rack/cabinet in the room and I figured I could center it so that it had plenty of space on all sides. The rack I'm looking at is a SMC rack on casters with fully perforated rear door, fan at the top, and perforated sides on either side of the front door's plexiglass. Consider removing the doors (or not ordering them); you'll get better air circulation. If you do order a rack, get roll-out shelves for towers, UPS, etc - i.e., everything heavy. Consider how you will service a tower whose access panel is on the side. With a 42U rack/cabinet, I think I could guarantee at least 1U of space between each component. I didn't notice any component giving off much heat other than the UPS's. Are any of these passively cooled devices? If not, space between racks should not be an issue, each component should be self-sufficient in cooing providing the ambient (intake) air temp is low enough. I realize this is no where near the ideal data center, but I don't think the hardware/application demands that type of setup, right? Only you (or your bosses) can decide how critical the application is and how much money to spend on protecting it. Same environment, smaller scale. I suggest you talk to the building engineer (if such exists) for ideas and suggestions. You may be building a sauna. |
|
Thread Tools | |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Thread Starter | Forum | Replies | Last Post |
rack mount question | legion | Homebuilt PC's | 8 | October 26th 04 09:23 PM |
Freedom: Coming to a Windows Box Near You | Ablang | General | 0 | June 30th 04 03:04 AM |
SCO: IBM trying to hijack Open Source says supporter | Daeron | Homebuilt PC's | 6 | February 11th 04 01:10 AM |
cdrw tray won't open with physical button but WILL open with Eject in Explorer | RegularJoe | Homebuilt PC's | 3 | January 24th 04 06:29 PM |
Liteon CD-RW 52x24x52 -- tray won't open w/ CD-RW disc? (Model LTR-52246S) | Scott Carson | Cdr | 4 | September 4th 03 11:39 PM |