Are any of the adjoining spaces unoccupied? Perhaps, you could put a
window A/C through a wall and dump the heat 'next door'.


The room is surrounded by an office, a storage room, and the office hallway.
I don't think blowing a hole in the wall will be well-seen by the company
execs or building management.

Others have recommended a fan in place of a ceiling tile. I've never seen
any of these around. Anyone used these before? Would they work for this
application? I figure the HVAC vent will bring in cold air while the fan
could take out the cold air.

--
Yoann Roman


  #12  
Old September 9th 05, 04:54 PM
Yoann Roman
external usenet poster
 
Posts: n/a
Default

My main concerns a
- to protect the equipment from general dust


Air filtration can be necessary. Could be whole-room, could
be on a sealed cabinet, either way if this is a dusty
environment then a service interval needs to be maintained
for the filter inspection and/or replacement.



It's not too dusty, really. Right now, the equipment is housed in a regular
office, which is probably the source of most of the dust. I figure that once
this is in an isolated room, the dust will reduce significantly. The
enclosed cabinet was an additional precaution.

- provide a stable physical environment (safe from bumps, hits,
etc...)


If people are getting in and hitting the racks, you need
better locks or a guard or pre-employment screening or
something of this nature.


The room is also the telco room, so telco guys may accidently hit against
the equipment when working in that room. It's really more of a closet, so
there isn't too much space. It should be fine, but, again, precautionary.

- have a setup that allows easy maintenance and setup, but nothing
regular
- protect against accidental pulling of cables (the room is also the
telco closet open to telco companies)


You can partition things off, demand a telco check-in and
supervision, or have insurance cover any damage, yours or
theirs. It's not a large room so is there even space for
everything you need in it and still the realistic
expectation that a stranger can walk in and service
something? Depends on where you situate everything. We
can't easily do that or advise on it.



From my measurements, space shouldn't be too big a problem. There's only
going to be one rack inside the entire room. The telco stuff is all
wall-mounted and takes up basically no space. The note about preventing
accidental pulling of cables is that, once we know the telco guy is in
there, we don't watch over him/her 24/7. It's too small a room to do so. So,
while they're not idiots, I just want to be cautious.

This is a small/medium business, as you can tell by the number of
servers, so cost is the key. Dedicated HVAC is probably hard to
obtain from the building. Regular HVAC is never shut off during the
year, though. There will be a duct added to the room.


I suggest not only a duct but fan local to the room.



I take it this fan would take air out of the room. How would you suggest
installing this? The room is surrounded by an office, a storage room, and
the main office hallway. It has no windows. It does have an acoustic
ceiling, so I could place a fan there, but I haven't come across any such
models.

If air flow became a problem, maybe some of APC's air flow products
would help, although the room has no raised floor. It has tiled
ceilings, but I don't think there is much air circulation up there.


There's where a fan comes in. If the fan is exhausting into
the ceiling, then there is air circulation... providing the
room isn't so sealed off that no air gets in but HVAC duct
will help there too. In other words with a localized AC
system the room can be fairly well sealed (except the
back-end of the AC unit itself) but without localized AC,
you'll want the room not so well sealed up, meaning typical
doors over carpeted areas are too much restriction without
*something* else to allow that flow while still keeping the
room secure.


The room does not have localized A/C, but it does have its own HVAC vent. It
is not sealed off very well. There is a fairly large gap under the door that
can aid in air circulation. I'm thinking that a fan in the ceiling may help,
but I'm not sure where to buy such a device.

This will be the only
rack/cabinet in the room and I figured I could center it so that it
had plenty of space on all sides. The rack I'm looking at is a SMC
rack on casters with fully perforated rear door, fan at the top, and
perforated sides on either side of the front door's plexiglass.

With a 42U rack/cabinet, I think I could guarantee at least 1U of
space between each component. I didn't notice any component giving
off much heat other than the UPS's.


Are any of these passively cooled devices? If not, space
between racks should not be an issue, each component should
be self-sufficient in cooing providing the ambient (intake)
air temp is low enough.


One of the switches has no fan (I figured that's what you meant by passively
cooled device). The rest of the equipment has fans, but I've typically been
recommended to have 1U of space between switches/routers and the such. Not
so much with servers, but I plan on doing it anyway as a precautionary
measure, if I have the room.

I realize this is no where near the ideal data center, but I don't
think the hardware/application demands that type of setup, right?


Same environment, smaller scale.


My reason for this comment was cost, really. This is a small business, so
cost is a very important factor. Second, this room already exists and has
already been in use for the DMARC and other telco equipment. I'm just
relocating the server equipment into it. Lastly, the room is very close to
offices and off the main hallway, so noise is an issue. I don't want to put
in an air conditioning unit that makes it sound like the room will collapse.
The servers, all combine, aren't noisy enough themselves.

Thanks for the advice/time.

--
Yoann Roman


  #13  
Old September 9th 05, 07:16 PM
kony
external usenet poster
 
Posts: n/a
Default

On Fri, 9 Sep 2005 11:45:32 -0400, "Yoann Roman"
wrote:

Are any of the adjoining spaces unoccupied? Perhaps, you could put a
window A/C through a wall and dump the heat 'next door'.


The room is surrounded by an office, a storage room, and the office hallway.
I don't think blowing a hole in the wall will be well-seen by the company
execs or building management.


The company execs then, will need adequately briefed about
the need for the room to be suitable for the purpose... IF
whatever you decide to do requires modifications.



Others have recommended a fan in place of a ceiling tile. I've never seen
any of these around. Anyone used these before? Would they work for this
application? I figure the HVAC vent will bring in cold air while the fan
could take out the cold air.


Such a fan should have a bracket and be supported from
above, not just a hole cut into a ceiling tile (if that were
what you were thinking of based on my non-descript concept).
Would just a hole work? Maybe, but I wouldn't count on it
without knowing the rigidity of the ceiling or any other
unforeen variables... I'd plan on a very secure mounting.
As for building management, they might not like a fan
either, you might have someone keen to lease/legal issues
look over details this impinge... in other words such a
project should be done with all having full knowledge of it.


  #14  
Old September 10th 05, 05:08 AM
Bennett Price
external usenet poster
 
Posts: n/a
Default

I think there's some confusion about air circulation and HVAC. Often,
the space above a drop ceiling is an air plenum, pulling 'used' air back
to the fans (and heating/cooling equipment) for the building. At other
times, duct work is used to pull the air back (return air as its
called); in this case the space above the ceiling tiles is just dead
space. You've got to determine whether your ceiling is a return plenum
or whether it is just dead space. Go into a room near your proposed
server room that has two grills, probably one in the room's center and
one at the periphery. The center one is probably supplying air while
the one at the edge is probably pulling out 'used' air. A Kleenex on a
stick will show which way the air flows. Then investigate whether the
return air grill is tied to duct work or is just a hole in the ceiling.
If you have an active plenum, then one supply duct at one end of the
server closet and a hole in the ceiling at the other end might provide
sufficient ventilation. If the ceiling is dead and a return duct can't
be installed, perhaps louvers in the door would let the heated air
escape. Putting a fan in the ceiling blowing up might help a little but
I wouldn't count on it. Just get a $20 box fan at K-Mart, cut a hole in
the ceiling tile, and lay the fan on the tile. If you want, you can tie
some strings to the fan and to the ceiling tile hangers for extra security.

And I repeat an earlier question - do you know for sure that the
building will be supplying cold air during the heating season?

Yoann Roman wrote:
My main concerns a
- to protect the equipment from general dust


Air filtration can be necessary. Could be whole-room, could
be on a sealed cabinet, either way if this is a dusty
environment then a service interval needs to be maintained
for the filter inspection and/or replacement.




It's not too dusty, really. Right now, the equipment is housed in a regular
office, which is probably the source of most of the dust. I figure that once
this is in an isolated room, the dust will reduce significantly. The
enclosed cabinet was an additional precaution.


- provide a stable physical environment (safe from bumps, hits,
etc...)


If people are getting in and hitting the racks, you need
better locks or a guard or pre-employment screening or
something of this nature.



The room is also the telco room, so telco guys may accidently hit against
the equipment when working in that room. It's really more of a closet, so
there isn't too much space. It should be fine, but, again, precautionary.


- have a setup that allows easy maintenance and setup, but nothing
regular
- protect against accidental pulling of cables (the room is also the
telco closet open to telco companies)


You can partition things off, demand a telco check-in and
supervision, or have insurance cover any damage, yours or
theirs. It's not a large room so is there even space for
everything you need in it and still the realistic
expectation that a stranger can walk in and service
something? Depends on where you situate everything. We
can't easily do that or advise on it.




From my measurements, space shouldn't be too big a problem. There's only
going to be one rack inside the entire room. The telco stuff is all
wall-mounted and takes up basically no space. The note about preventing
accidental pulling of cables is that, once we know the telco guy is in
there, we don't watch over him/her 24/7. It's too small a room to do so. So,
while they're not idiots, I just want to be cautious.


This is a small/medium business, as you can tell by the number of
servers, so cost is the key. Dedicated HVAC is probably hard to
obtain from the building. Regular HVAC is never shut off during the
year, though. There will be a duct added to the room.


I suggest not only a duct but fan local to the room.




I take it this fan would take air out of the room. How would you suggest
installing this? The room is surrounded by an office, a storage room, and
the main office hallway. It has no windows. It does have an acoustic
ceiling, so I could place a fan there, but I haven't come across any such
models.


If air flow became a problem, maybe some of APC's air flow products
would help, although the room has no raised floor. It has tiled
ceilings, but I don't think there is much air circulation up there.


There's where a fan comes in. If the fan is exhausting into
the ceiling, then there is air circulation... providing the
room isn't so sealed off that no air gets in but HVAC duct
will help there too. In other words with a localized AC
system the room can be fairly well sealed (except the
back-end of the AC unit itself) but without localized AC,
you'll want the room not so well sealed up, meaning typical
doors over carpeted areas are too much restriction without
*something* else to allow that flow while still keeping the
room secure.



The room does not have localized A/C, but it does have its own HVAC vent. It
is not sealed off very well. There is a fairly large gap under the door that
can aid in air circulation. I'm thinking that a fan in the ceiling may help,
but I'm not sure where to buy such a device.


This will be the only
rack/cabinet in the room and I figured I could center it so that it
had plenty of space on all sides. The rack I'm looking at is a SMC
rack on casters with fully perforated rear door, fan at the top, and
perforated sides on either side of the front door's plexiglass.

With a 42U rack/cabinet, I think I could guarantee at least 1U of
space between each component. I didn't notice any component giving
off much heat other than the UPS's.


Are any of these passively cooled devices? If not, space
between racks should not be an issue, each component should
be self-sufficient in cooing providing the ambient (intake)
air temp is low enough.



One of the switches has no fan (I figured that's what you meant by passively
cooled device). The rest of the equipment has fans, but I've typically been
recommended to have 1U of space between switches/routers and the such. Not
so much with servers, but I plan on doing it anyway as a precautionary
measure, if I have the room.


I realize this is no where near the ideal data center, but I don't
think the hardware/application demands that type of setup, right?


Same environment, smaller scale.



My reason for this comment was cost, really. This is a small business, so
cost is a very important factor. Second, this room already exists and has
already been in use for the DMARC and other telco equipment. I'm just
relocating the server equipment into it. Lastly, the room is very close to
offices and off the main hallway, so noise is an issue. I don't want to put
in an air conditioning unit that makes it sound like the room will collapse.
The servers, all combine, aren't noisy enough themselves.

Thanks for the advice/time.

  #15  
Old September 10th 05, 04:09 PM
Yoann Roman
external usenet poster
 
Posts: n/a
Default

I think there's some confusion about air circulation and HVAC. Often,
the space above a drop ceiling is an air plenum, pulling 'used' air
back
to the fans (and heating/cooling equipment) for the building. At
other times, duct work is used to pull the air back (return air as its
called); in this case the space above the ceiling tiles is just dead
space. You've got to determine whether your ceiling is a return plenum
or whether it is just dead space. Go into a room near your proposed
server room that has two grills, probably one in the room's center and
one at the periphery. The center one is probably supplying air while
the one at the edge is probably pulling out 'used' air. A Kleenex on
a
stick will show which way the air flows. Then investigate whether the
return air grill is tied to duct work or is just a hole in the
ceiling.
If you have an active plenum, then one supply duct at one end of the
server closet and a hole in the ceiling at the other end might provide
sufficient ventilation. If the ceiling is dead and a return duct
can't
be installed, perhaps louvers in the door would let the heated air
escape. Putting a fan in the ceiling blowing up might help a little
but
I wouldn't count on it. Just get a $20 box fan at K-Mart, cut a hole
in
the ceiling tile, and lay the fan on the tile. If you want, you can
tie
some strings to the fan and to the ceiling tile hangers for extra
security.

And I repeat an earlier question - do you know for sure that the
building will be supplying cold air during the heating season?


Thanks for the clarifications. This helps a lot!

I'll check on the active plenum vs. return vents. From what I've seen by
poking around, there are a few ceiling tiles that are just perforated and
have no duct work attached up in the ceiling. I don't know if these are
potential HVAC ducts that have not been hooked up or proof of an active
plenum.

I doubt they will be supplying cold air during the heating season.
Unfortunately, the building duct work isn't advanced enough to separate hot
& cold vents. I did change my decision and will now use open racks. I figure
if it gets too hot during winter, I can just block off the vent and install
a fan into the ceiling like suggested.

Thanks again for the tips.

--
Yoann Roman


  #16  
Old September 10th 05, 06:34 PM
Bennett Price
external usenet poster
 
Posts: n/a
Default



Yoann Roman wrote:
I think there's some confusion about air circulation and HVAC. Often,
the space above a drop ceiling is an air plenum, pulling 'used' air
back
to the fans (and heating/cooling equipment) for the building. At
other times, duct work is used to pull the air back (return air as its
called); in this case the space above the ceiling tiles is just dead
space. You've got to determine whether your ceiling is a return plenum
or whether it is just dead space. Go into a room near your proposed
server room that has two grills, probably one in the room's center and
one at the periphery. The center one is probably supplying air while
the one at the edge is probably pulling out 'used' air. A Kleenex on
a
stick will show which way the air flows. Then investigate whether the
return air grill is tied to duct work or is just a hole in the
ceiling.
If you have an active plenum, then one supply duct at one end of the
server closet and a hole in the ceiling at the other end might provide
sufficient ventilation. If the ceiling is dead and a return duct
can't
be installed, perhaps louvers in the door would let the heated air
escape. Putting a fan in the ceiling blowing up might help a little
but
I wouldn't count on it. Just get a $20 box fan at K-Mart, cut a hole
in
the ceiling tile, and lay the fan on the tile. If you want, you can
tie
some strings to the fan and to the ceiling tile hangers for extra
security.

And I repeat an earlier question - do you know for sure that the
building will be supplying cold air during the heating season?



Thanks for the clarifications. This helps a lot!

I'll check on the active plenum vs. return vents. From what I've seen by
poking around, there are a few ceiling tiles that are just perforated and
have no duct work attached up in the ceiling. I don't know if these are
potential HVAC ducts that have not been hooked up or proof of an active
plenum.

I doubt they will be supplying cold air during the heating season.
Unfortunately, the building duct work isn't advanced enough to separate hot
& cold vents. I did change my decision and will now use open racks. I figure
if it gets too hot during winter, I can just block off the vent and install
a fan into the ceiling like suggested.

Thanks again for the tips.


Installing a fan in the ceiling will not help very much unless you have
a supply of cool air from somewhere. Consider louvers in the door as a
source of cool (70F) supply air during the winter. Keep in mind that to
ventilate your heat sources you need to supply cool air to the closet
and suck out hot air from the closet.

I urge you to get some expert help on this. Convince your bosses that a
proper environment is a legitimate cost of business, just as the
computers are. And don't forget to add the lighting in the closet as
yet another heat source.
 




Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
rack mount question legion Homebuilt PC's 8 October 26th 04 09:23 PM
Freedom: Coming to a Windows Box Near You Ablang General 0 June 30th 04 03:04 AM
SCO: IBM trying to hijack Open Source says supporter Daeron Homebuilt PC's 6 February 11th 04 01:10 AM
cdrw tray won't open with physical button but WILL open with Eject in Explorer RegularJoe Homebuilt PC's 3 January 24th 04 06:29 PM
Liteon CD-RW 52x24x52 -- tray won't open w/ CD-RW disc? (Model LTR-52246S) Scott Carson Cdr 4 September 4th 03 11:39 PM


All times are GMT +1. The time now is 11:31 PM.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 HardwareBanter.
The comments are property of their posters.