Defunct batteries on APC Smart UPS 1000



 
 
Thread Tools Display Modes
  #1  
Old July 31st 10, 08:13 AM posted to alt.comp.hardware
Brian Cryer[_2_]
external usenet poster
 
Posts: 84
Default Defunct batteries on APC Smart UPS 1000

I recently purchased a second hand APC Smart UPS 1000 on ebay - when it
arrived it was totally dead. (Seller gave a full no-quibble refund which was
nice.) Having done some research the most likely cause seemed to be the
batteries - if the unit thinks the batteries are dead then it won't turn on.
Taking it to work and temporarily swapping the battery with an identical
unit at work revealed this to be the case.

The replacement batteries (even non-branded ones) are not cheap, so I was
wondering whether its worth looking at either of the following two options -
or am I just wasting time (and money) and is it better to just buy new
batteries?

1. It takes two 12v sealed lead-acid batteries which are glued together
(strong glue!) so they can be handled pretty much as a single unit, but
there are two of them. I think the unit was probably left on the shelf for a
long time and has discharged (because I get the impression that it worked
the last time it was used). One of the batteries reads at 3v the other at
9v. So is it worth trying to charge these externally to the UPS to see if
they will rechange? If so how? can I use a car battery charger or do I need
something specialised?

2. Since the two batteries read 3v and 9v, is it viable/sensible to replace
the 3v one and keep the 9v one (hoping it will charge and come up to 12v)?
This would be about half the replacement cost, but I don't know whether
mixing new and old batteries like this is a good or a bad thing.

Thanks in advance.
--
Brian Cryer
http://www.cryer.co.uk/brian

  #2  
Old July 31st 10, 02:02 PM posted to alt.comp.hardware
Gerard Bok
external usenet poster
 
Posts: 177
Default Defunct batteries on APC Smart UPS 1000

On Sat, 31 Jul 2010 08:13:45 +0100, "Brian Cryer"
not.here@localhost wrote:

I recently purchased a second hand APC Smart UPS 1000 on ebay - when it
arrived it was totally dead.


1. It takes two 12v sealed lead-acid batteries which are glued together
One of the batteries reads at 3v the other at
9v. So is it worth trying to charge these externally to the UPS to see if
they will rechange? If so how? can I use a car battery charger or do I need
something specialised?


If they are (sealed) lead acid batteries, you can use a normal
car battery charger. Keep away from those 'fast blasters' though.
(Those may come in handy if you need to juice a 200 Ah car
battery in 10 minutes, but they may blow your 30 Ah UPS
batteries.) Limit the charge current to say c / 10.
That makes 3 amps for a 30 Ah battery.

2. Since the two batteries read 3v and 9v, is it viable/sensible to replace
the 3v one and keep the 9v one (hoping it will charge and come up to 12v)?


No. Never replace 'half a battery'. It's just a waste.
(I wouldn't even be surprised if batteries are paired in the
factory before they get glued together !)

But it doesn't hurt charging the old batteries both till 'full'
and see how they behave.
You can still replace them if they prove not to be useful.

--
Kind regards,
Gerard Bok
  #3  
Old August 1st 10, 07:53 AM posted to alt.comp.hardware
Brian Cryer[_2_]
external usenet poster
 
Posts: 84
Default Defunct batteries on APC Smart UPS 1000

"Gerard Bok" wrote in message
...
On Sat, 31 Jul 2010 08:13:45 +0100, "Brian Cryer"
not.here@localhost wrote:

I recently purchased a second hand APC Smart UPS 1000 on ebay - when it
arrived it was totally dead.


1. It takes two 12v sealed lead-acid batteries which are glued together
One of the batteries reads at 3v the other at
9v. So is it worth trying to charge these externally to the UPS to see if
they will rechange? If so how? can I use a car battery charger or do I
need
something specialised?


If they are (sealed) lead acid batteries, you can use a normal
car battery charger. Keep away from those 'fast blasters' though.
(Those may come in handy if you need to juice a 200 Ah car
battery in 10 minutes, but they may blow your 30 Ah UPS
batteries.) Limit the charge current to say c / 10.
That makes 3 amps for a 30 Ah battery.

2. Since the two batteries read 3v and 9v, is it viable/sensible to
replace
the 3v one and keep the 9v one (hoping it will charge and come up to 12v)?


No. Never replace 'half a battery'. It's just a waste.
(I wouldn't even be surprised if batteries are paired in the
factory before they get glued together !)

But it doesn't hurt charging the old batteries both till 'full'
and see how they behave.
You can still replace them if they prove not to be useful.

--
Kind regards,
Gerard Bok


Thanks Gerard. I've put the batteries on charge, but they clearly aren't
charging so it looks like I'll need to buy new ones.
--
Brian Cryer
http://www.cryer.co.uk/brian


  #4  
Old August 1st 10, 04:11 PM posted to alt.comp.hardware
Sjouke Burry[_2_]
external usenet poster
 
Posts: 192
Default Defunct batteries on APC Smart UPS 1000

Brian Cryer wrote:
"Gerard Bok" wrote in message
...
On Sat, 31 Jul 2010 08:13:45 +0100, "Brian Cryer"
not.here@localhost wrote:

I recently purchased a second hand APC Smart UPS 1000 on ebay - when it
arrived it was totally dead.
1. It takes two 12v sealed lead-acid batteries which are glued together
One of the batteries reads at 3v the other at
9v. So is it worth trying to charge these externally to the UPS to see if
they will rechange? If so how? can I use a car battery charger or do I
need
something specialised?

If they are (sealed) lead acid batteries, you can use a normal
car battery charger. Keep away from those 'fast blasters' though.
(Those may come in handy if you need to juice a 200 Ah car
battery in 10 minutes, but they may blow your 30 Ah UPS
batteries.) Limit the charge current to say c / 10.
That makes 3 amps for a 30 Ah battery.

2. Since the two batteries read 3v and 9v, is it viable/sensible to
replace
the 3v one and keep the 9v one (hoping it will charge and come up to 12v)?

No. Never replace 'half a battery'. It's just a waste.
(I wouldn't even be surprised if batteries are paired in the
factory before they get glued together !)

But it doesn't hurt charging the old batteries both till 'full'
and see how they behave.
You can still replace them if they prove not to be useful.

--
Kind regards,
Gerard Bok


Thanks Gerard. I've put the batteries on charge, but they clearly aren't
charging so it looks like I'll need to buy new ones.

If they are suphated(the plates), it sometimes helps,
to put a high voltage on them.
Rectify the mains, put a hetaer elements or big lamp in series with
it, and feed the battery for a few minutes, or until the series device
shows activity (lamp fully burning ot heater getting hot).
Then try again to charge.
  #5  
Old August 3rd 10, 07:46 PM posted to alt.comp.hardware
Brian Cryer[_2_]
external usenet poster
 
Posts: 84
Default Defunct batteries on APC Smart UPS 1000

"Sjouke Burry" wrote in message
...
Brian Cryer wrote:
"Gerard Bok" wrote in message
...
On Sat, 31 Jul 2010 08:13:45 +0100, "Brian Cryer"
not.here@localhost wrote:

I recently purchased a second hand APC Smart UPS 1000 on ebay - when it
arrived it was totally dead.
1. It takes two 12v sealed lead-acid batteries which are glued together
One of the batteries reads at 3v the other at
9v. So is it worth trying to charge these externally to the UPS to see
if
they will rechange? If so how? can I use a car battery charger or do I
need
something specialised?
If they are (sealed) lead acid batteries, you can use a normal
car battery charger. Keep away from those 'fast blasters' though.
(Those may come in handy if you need to juice a 200 Ah car
battery in 10 minutes, but they may blow your 30 Ah UPS
batteries.) Limit the charge current to say c / 10.
That makes 3 amps for a 30 Ah battery.

2. Since the two batteries read 3v and 9v, is it viable/sensible to
replace
the 3v one and keep the 9v one (hoping it will charge and come up to
12v)?
No. Never replace 'half a battery'. It's just a waste.
(I wouldn't even be surprised if batteries are paired in the
factory before they get glued together !)

But it doesn't hurt charging the old batteries both till 'full'
and see how they behave.
You can still replace them if they prove not to be useful.

--
Kind regards,
Gerard Bok


Thanks Gerard. I've put the batteries on charge, but they clearly aren't
charging so it looks like I'll need to buy new ones.

If they are suphated(the plates), it sometimes helps,
to put a high voltage on them.
Rectify the mains, put a hetaer elements or big lamp in series with
it, and feed the battery for a few minutes, or until the series device
shows activity (lamp fully burning ot heater getting hot).
Then try again to charge.


Thank you for the suggestion. This might be the perfect solution, but its
way outside my comfort zone. (I just don't like touching the mains.)
--
Brian Cryer
http://www.cryer.co.uk/brian



 




Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

vB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
APC UPS Batteries Marc[_7_] General 2 June 23rd 09 08:57 AM
APC Smart ups SUA1500 and auto restart not working on server withindependent NIC... markm75 General 0 December 13th 07 05:30 PM
External batteries on an APC RS1500 UPS (BR1500)? [email protected] General 3 November 13th 07 01:52 AM
APC battery UPS? Ablang General 8 February 3rd 04 02:28 AM
APC UPS BACK UPS XS 1500 external battery recognition? denton General 0 August 2nd 03 06:14 PM


All times are GMT +1. The time now is 06:29 AM.


Powered by vBulletin® Version 3.6.4
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 HardwareBanter.
The comments are property of their posters.